I apologize as this is not a programming issue directly however I am sure here is very experienced Hardware people and I am asking a bit of help on a transistor circuit.
I need to handle on a machine an emergency stop button which is wired to a 24V supply ,I was thinking to use a transistor inverted signal to the mcu pin
however this has brought 2 questions to my mind
(1) What is the easiest way to calculate the value of the base resistor?
(2) can this circuit be improved to handle reverse polarity condition ?
I do apologize for this elementary questions I am no hardware developer and I want to make sure that what I am doing is ok and safe I will appreciate any help and any other suggestion to handle the emergency stop button
Many thanks
Help on a circuit
- QMESAR
- Valued Contributor
- Posts: 1287
- Joined: Sun Oct 05, 2014 3:20 pm
- Location: Russia
- Has thanked: 384 times
- Been thanked: 614 times
- Contact:
Help on a circuit
- Attachments
-
- 1.JPG (11.79 KiB) Viewed 5068 times
https://www.flowcodexchange.com/
Regards QMESAR
Regards QMESAR
- Steve001
- Valued Contributor
- Posts: 1189
- Joined: Wed Dec 31, 2008 3:37 pm
- Has thanked: 460 times
- Been thanked: 523 times
- Contact:
Re: Help on a circuit
Hi Peter
Looking at a bog standard BC107 for example
http://www.farnell.com/datasheets/16619 ... 1485678472
Working on worst case scenarios
The information shows that this has a minimum current gain of 40 (hfe)
Using your 10K collector resistor
I= V/R
I= 5/10000
I= 0.5 mA
You can calculate Ib now
Ib=Ic/hfe
Ib=0.0005/40
Ib= 0.0000125
Ib= 0.0000125= 0.0125 mA
R= V/I
R= 24/0.0000125
R= 2.4 MΩ
this is how i do it there are other ways to do base biasing using a potential divider this helps the issues with the differences with the transistors hfe range.
Because the input is 24 volts i would use an opto because of the large size of base resistor and also the voltage level.
there is this too may help
http://www.nutsvolts.com/magazine/artic ... ook_part_1
to handle the reverse polarity is this the transistor base ?
i would use a small diode 1N4148 or similar dont forget the diode forward volt drop when calculating resistors
one of our suppliers of ups's / static switches uses an opto isolator for the emergency shut down input that is energised healthy so if any problem ie wire comes off then the unit shuts down.
Using an AC input opto isolator this would do your reverse polarity also
http://www.vishay.com/optocouplers/opto-ac-in/
hope this helps
Steve
Looking at a bog standard BC107 for example
http://www.farnell.com/datasheets/16619 ... 1485678472
Working on worst case scenarios
The information shows that this has a minimum current gain of 40 (hfe)
Using your 10K collector resistor
I= V/R
I= 5/10000
I= 0.5 mA
You can calculate Ib now
Ib=Ic/hfe
Ib=0.0005/40
Ib= 0.0000125
Ib= 0.0000125= 0.0125 mA
R= V/I
R= 24/0.0000125
R= 2.4 MΩ
this is how i do it there are other ways to do base biasing using a potential divider this helps the issues with the differences with the transistors hfe range.
Because the input is 24 volts i would use an opto because of the large size of base resistor and also the voltage level.
there is this too may help
http://www.nutsvolts.com/magazine/artic ... ook_part_1
to handle the reverse polarity is this the transistor base ?
i would use a small diode 1N4148 or similar dont forget the diode forward volt drop when calculating resistors
one of our suppliers of ups's / static switches uses an opto isolator for the emergency shut down input that is energised healthy so if any problem ie wire comes off then the unit shuts down.
Using an AC input opto isolator this would do your reverse polarity also
http://www.vishay.com/optocouplers/opto-ac-in/
hope this helps
Steve
Success always occurs in private and failure in full view.
- QMESAR
- Valued Contributor
- Posts: 1287
- Joined: Sun Oct 05, 2014 3:20 pm
- Location: Russia
- Has thanked: 384 times
- Been thanked: 614 times
- Contact:
Re: Help on a circuit
Hi Steve
I do not now how to thank you for sharing your valuable knowledge ,All I can do is say really a true thank you very much,
and hope one day I can roll a stone out of your way.Once again thank you very much ,This is a very good example and made it easy for me to understand
Regards
Peter
I do not now how to thank you for sharing your valuable knowledge ,All I can do is say really a true thank you very much,
and hope one day I can roll a stone out of your way.Once again thank you very much ,This is a very good example and made it easy for me to understand
Regards
Peter
https://www.flowcodexchange.com/
Regards QMESAR
Regards QMESAR
-
- Posts: 315
- Joined: Sun Jun 23, 2013 1:29 pm
- Has thanked: 28 times
- Been thanked: 61 times
- Contact:
Re: Help on a circuit
Hi QMESAR,
I completely concur with Steve's advice concerning the use of an Opto Isolator and emergency fail safe procedure.
The use of an Opto Isolator what be beneficial when monitoring 'outside' voltages as Steve said but also to completely isolate the micro-controller pin from the outside world.
I'm guessing you are just monitoring the emergency circuit but in case you are involved with anything more please allow me to impart a little background info. By trade I'm an electrician (who did electronics 30 yrs ago but changed career), when I've been involved with an industrial electrical installation, GENERALLY, there have been two main designs when dealing with emergency cut off switching. The first has been installed by the manufacturer of the machine, which cuts the supply to the machine locally. The second system (basically) is when there is a series circuit connected via a number of locking switches around a workshop, which connects to a contactor's coil and keeps the contactor energised which feeds all the the machines. However, in practice there a little more to it than what I have described above ie self feeding contactor circuits etc
As a general rule of thumb an EMERGENCY SWITCHING SYSTEM switches off power and it cannot be restored with specific human intervention and is often controlled/regulated by country specific legal regulations.
Doc
I completely concur with Steve's advice concerning the use of an Opto Isolator and emergency fail safe procedure.
The use of an Opto Isolator what be beneficial when monitoring 'outside' voltages as Steve said but also to completely isolate the micro-controller pin from the outside world.
I'm guessing you are just monitoring the emergency circuit but in case you are involved with anything more please allow me to impart a little background info. By trade I'm an electrician (who did electronics 30 yrs ago but changed career), when I've been involved with an industrial electrical installation, GENERALLY, there have been two main designs when dealing with emergency cut off switching. The first has been installed by the manufacturer of the machine, which cuts the supply to the machine locally. The second system (basically) is when there is a series circuit connected via a number of locking switches around a workshop, which connects to a contactor's coil and keeps the contactor energised which feeds all the the machines. However, in practice there a little more to it than what I have described above ie self feeding contactor circuits etc
As a general rule of thumb an EMERGENCY SWITCHING SYSTEM switches off power and it cannot be restored with specific human intervention and is often controlled/regulated by country specific legal regulations.
Doc
- QMESAR
- Valued Contributor
- Posts: 1287
- Joined: Sun Oct 05, 2014 3:20 pm
- Location: Russia
- Has thanked: 384 times
- Been thanked: 614 times
- Contact:
Re: Help on a circuit
Hi Docara.
Thank you for your information,Luckily only need to monitor the Emergency circuit to stop SW execution for some parts however the main safety circuits for the machine are handled by the original equipment
Thank you for your information,Luckily only need to monitor the Emergency circuit to stop SW execution for some parts however the main safety circuits for the machine are handled by the original equipment
https://www.flowcodexchange.com/
Regards QMESAR
Regards QMESAR